11/11/2016 3:11 PM | |
Posts: 439 Rating: (108) |
Salut, The sensor you are using provide 0...10V, as you can see in the manufacturer website. As you can see in the properties of the onboard analog input, they are 0...10V. Go in "Device configuration" of you PLC, select the PLC in the "Device view", go in "Properties" and select "IO tags" tab. You will see two IW address, those are your analog input address. Wire your sensor correctly, add those address into your "Watch table" and you will see the value change with the pressure. Best regards, Hugo AttachmentAnalog input.zip (122 Downloads) |
Last edited by: HugoD at: 11/11/2016 3:12:11 PM |
|
11/15/2016 5:14 PM | |
Posts: 439 Rating: (108) |
Hello, Try it and let us know. See attach part of the manual. I tell my customer to follow the recommandation of the manual for their industrial application, if they don't follow them the result is unsure. Best regards, Hugo AttachmentUsing a memory card.pdf (62 Downloads) |
Last edited by: HugoD at: 11/15/2016 5:17:49 PMLast edited by: HugoD at: 11/15/2016 5:19:17 PMLast edited by: HugoD at: 11/15/2016 5:20:50 PM |
|