Hello, in my opinion is this not a good idea to wire the external signals direct to the PLC. I would connect the 2 machines with optocoupler . Solid-state relay module - PLC-OPT- 24DC/ 48DC/100/SEN - 2900358 If you use this coupler you have no problems with different potentials, current over the Ground connection, overvoltage and more. This solution is not the cheapest but safe. regards |