9/17/2013 8:39 AM | |
Joined: 1/21/2013 Last visit: 3/19/2024 Posts: 4618 Rating: (705) |
Hi Take a look at page 50: MICROMASTER Vector MIDIMASTER Vector - Siemens try to see if he can do this function, otherwise you have to do it yourself. |
Last edited by: Ste39 at: 9/17/2013 9:20 AM |
|
9/17/2013 2:39 PM | |
Joined: 4/22/2010 Last visit: 2/15/2024 Posts: 5697 Rating: (711) |
Hello, Also have a look at this FAQ: MICROMASTER 4: Can I also use pushbuttons (without relay interconnection) to control my MICROMASTER? Regards, Marcjan |
Problem solved? |
|
This contribution was helpful to1 thankful Users |
9/17/2013 3:19 PM | |
Posts: 7 Rating: (0) |
Hi Ste39. My German is not what it should be. That doesn't appear to be my inverter though. Here's a copy of the manual. http://www.mawos.com.pl/files/mmv_6se32_oi_en.pdf I played around with the inverter again yesterday and still no joy. The only way I can get the machine to run is by putting an On/Off rotary switch in the P+15V line(pin9). Then running that to a ON/OFF/ON toggle switch for my forward(DIN1 terminal 5 parameterP051 value[1])and reverse(DIN2 terminal 6 parameter P052 value[3]). I then have an emegency stop (DIN5 terminal 16 parameter P055 value[5]). Now I could run the machine with the rotary switch ON/OFF but I would prefer a standard Green ON Red OFF momentary switch set up. Thanks for your help. Steve. |
Last edited by: fishy-steve at: 9/17/2013 5:54 PM |
|
9/17/2013 4:41 PM | |
Joined: 1/21/2013 Last visit: 3/19/2024 Posts: 4618 Rating: (705) |
Hi steve, I think the only way is if you install a contactor and make the latching. |
9/17/2013 6:42 PM | |
Posts: 7 Rating: (0) |
Hi Marcjan. I did take a look at that before posting but didn't think it applied to my inverter. The highest parameter in my unit is up in the 900s??? Thanks for your help. Steve. |
9/18/2013 11:23 PM | |
Joined: 6/4/2008 Last visit: 4/23/2024 Posts: 1481 Rating: (322)
|
Hi Steve, Please see attached, I'm just throwing ideas at you here. I can't test this configuration as I've not seen one of these drives in nearly 10 years. The idea is to use the inbuilt relay to switch on as soon as the drive is running, meaning you can release the start button. Hence the single Start (ON) command instead of using ON Left and ON Right. As long as the OFF2 and OFF3 input signals are "healthy", the drive should start. The Reverse input must be selectable i.e. if you want forward, the contact is permanently open, and permanently closed for Reverse. Hope this helps, please let us know what your final solution was. Regards, Graeme AttachmentLathe.pdf (77 Downloads) |
This contribution was helpful to2 thankful Users |
Follow us on