Hello, I did a project in the past with the code reader MV320 and a comfort panel. You should put your post in the "SIMATIC Ident" section. First thing to know, the first IO field you put in a screen is the one that will be highlight when the page is open. So if you open a screen and do not select any IO field with your finger, scan a bar code, the result will be in the first IO field you dropped in TIA. There are bar code in the manual of the MV320 to configure the reader. (type of keyboard, add a carriage return etc...) If you configure it correctly, you should be able to plug the MV320 in your computer and the result of the scan can be display in a cell of Excel (like a usb keyboard). You can generate code via website, you just have to google the type of code you use with "generator". You will have to scan a specific barcode in the manual to be able to scan a barcode in your PC monitor. See attach functionnal project. I only had to use a IO field with string[60]. Best regards, Hugor AttachmentMV320 comfort panel OK.zip (418 Downloads) |