12/2/2016 1:17 PM | |
Posts: 10 Rating: (0) |
NAT How do I ping specifically please? |
12/2/2016 1:21 PM | |
Joined: 5/12/2006 Last visit: 11/14/2024 Posts: 22452 Rating: (3030)
|
Hello, ok with NAT you have a problem that the detect not working, here you must enter the IP manually in the adress field in TIA. Klick in the Adress Cell (Acess Adress in the first screen), enther the IP for the PLC and connect it. Note! Accessible Nodes also not working with NAT Mode! Must you use NAT Mode? Better in VM is to use the bridged mode, then TIA can find the direct connected devices because NAT block the search request from TIA! https://support.industry.siemens.com/cs/ww/en/view/78788417
Christoph |
Last edited by: ChristophD at: 12/2/2016 1:23:25 PM |
|
This contribution was helpful to1 thankful Users |
12/2/2016 1:22 PM | |
Posts: 310 Rating: (18) |
Hello, Just ping your ip in run . See the image . Regards, Arasan. |