9/9/2020 12:53 PM | |
Joined: 6/4/2010 Last visit: 9/11/2024 Posts: 387 Rating:
|
Dear Bruno, Yes, of course. You can scan all the BACnet devices and browse BACnet points from the Control Point (generic view) using the online workflow for 3rdparty devices and/or integrate it to be able to use them in the operations view for graphic, trending, alarming, etc. (See thelimitations mentioned in the documentation). General information about the Control Point can be found on SIOS under: https://support.industry.siemens.com/cs/ww/en/view/109780757 The Desigo Control Point engineering is described in the document A6V11604297. See chapter 2.4 on how to “Discover and assign devices”. Discover and assign devices The devices you want to operate and monitor must be assigned to the Desigo Control Point device.
The A6V11604297 Engineering documentation can be found under: Please note that the Beckhoff device has not been explicitly tested together with the PXM30.E. Best regards, Albis |
This contribution was helpful to
1 thankful Users |
Follow us on