Hi Autogen_7608052, You have to modify the “Time perid af all segments” and the “Max Size of all segments” The segments are stored in the project directory folder. < ProjectDirectory >ArchiveManager\TagLoggingFast < ProjectDirectory >ArchiveManager\TagLoggingSlow Form this folder you can check if the sements are created. For archive configuration you should make sure that the sum of all the single segments (Tag Logging Fast, Tag Logging Slow and Alarm Logging) does not exceed a certain number. See How many single segments can be connected to the SQL server in PCS 7 without impairing performance? https://support.industry.siemens.com/cs/ww/en/view/34473263 Best regards schufri AttachmentConfiguration.zip (31 Downloads) |