Hello AutoGen_5717228, The fault F30005 means that there is an overload in the application. In these cases, it is necessary to first check the wiring of the motor terminal box to ensure that it is at 230V or 400V, then check and if there are any doubts, restart the motor using the TIA Portal Startdrive wizard, entering all the motor data correctly and finally run the Motor ID (p1900 = 2) of the motor. If after doing all this the fault continues to appear, it will be necessary to use the Startdrive diagnostic tool called "Trace" and graph current consumption (r68), speed (r21) and temperature (r25). |