Can we use the Y-Link modul in order to connect standard DP-slave (e.g. SIMEAS Q) to both CPU318-2DP with Software Redundancy? Thanks. |
9/6/2005 11:07 AM | |
Joined: 8/10/2005 Last visit: 4/9/2024 Posts: 1486 Rating: (32)
|
Software redundancy can't use with Y-Link. This is not tested and there is no release. |