1/11/2012 9:30 AM | |
Joined: 4/4/2011 Last visit: 5/15/2025 Posts: 8 Rating:
|
Thanks, I will try your suggestion, |
1/11/2012 9:55 AM | |
Joined: 8/25/2006 Last visit: 9/12/2025 Posts: 2218 Rating:
|
You should order S00, then you will receive PIN (it is unique for each converter). Order number is 6RX1700-0AS00. |
1/11/2012 9:58 AM | |
Joined: 4/4/2011 Last visit: 5/15/2025 Posts: 8 Rating:
|
Thank you so much, good day |
1/11/2012 10:50 AM | |
Joined: 8/25/2006 Last visit: 9/12/2025 Posts: 2218 Rating:
|
You may set normalization of analog input 1 in P711= -100% and offset for it in P712=100%. Look in the manual, function diagram sheet G113. Then use P605=K0015. |
1/11/2012 11:09 AM | |
Joined: 4/4/2011 Last visit: 5/15/2025 Posts: 8 Rating:
|
thanks |
1/12/2012 5:38 PM | |
Joined: 4/4/2011 Last visit: 5/15/2025 Posts: 8 Rating:
|
Hi, Good day, I tried to run the drive with your suggested setting but have no success. Theres a variation of torque/current due to varrying of analog input to the drive. There have two analog output from the drive AO14=K115,AO16=K149 that are connected to analog input of the PLC as a feedback. I attached the configure software for 6RA24(original drive) and 6RA70(replacement drive) as well. Maybe it can help to pinpoint the cause of the problem. Thanks and regards, Franz AttachmentSimoreg.zip (403 Downloads) |