3/30/2012 7:52 AM | |
Posts: 49 Rating:
|
|
3/30/2012 8:33 AM | |||||||||||||
Posts: 49 Rating:
|
Hi Thanks for reply. parameters as follows.Voltage At Terminals is 405V Ac
|
||||||||||||
3/30/2012 11:38 AM | |
Joined: 8/25/2006 Last visit: 9/11/2025 Posts: 2218 Rating:
|
It seems you have see the function 'Automatic restart' in action. I.e. armature supply voltage drops below treshold (P351) for the time not longer than P086. You may read about it in themanual, chapter 9.17. |
3/31/2012 7:07 AM | |
Posts: 49 Rating:
|
dear sir P086-0.4sec. we noted that drive stayed in o4.0 state for longer time.
|
3/31/2012 11:04 AM | |
Joined: 8/25/2006 Last visit: 9/11/2025 Posts: 2218 Rating:
|
Hello. Ok, what type of drive you have? Simoreg DC-Master or Simoreg CM? When the drive stays in o4.0 for long time? Only after switch-on (ON command) or during operation? How long is this time? If this happen only after switch-on and takes not more than P089 (2 sec) - its normal. |
3/31/2012 12:24 PM | |
Posts: 49 Rating:
|
dear sir Drive details as: Type:1P6RA7075-6Dv62-0-Z Sr. no.:SZYA60905600065 Armature input:3AC 400V 175A 50/60Hz Output: DC 420V 270A Field Input:AC 400V 15A 50/60Hz Output: DC 325V 15A Issue A3/V3.2 As Run Command received By Drive o4.0 is initialised. it hold till run command on drive i.e. it may be more than 15sec and drive is not delivering output.
|
3/31/2012 12:40 PM | |
Joined: 8/25/2006 Last visit: 9/11/2025 Posts: 2218 Rating:
|
And you didn't get the fault F004 or F006? May you disable it in P820, please check this. I may recommend you to check the connections of gating pulses cables from board A7002 to the power section (X11-X16 and X21-X26). Or may be you can reset your drive to the factory settings (P051=21) and make a new comissioning. |