3/1/2024 2:39 PM | |
Joined: 3/27/2008 Last visit: 11/3/2024 Posts: 1144 Rating: (142) |
dip switches correct 0-10Volts, yes? P2000 = 60Hz Analogue input to terminals 3 & 4, is this potentiometer or reference Voltage? Check the following: r0752:0 = showing 0/10V range r0754:0= 0/100% P1000 = 2, analogue setpoint. refer to Function diagrams 2200 &2300 for analogue for setpoint Tractor AttachmentMM440 analogue input drg.pdf (470 Downloads) |
Tractor |
|
3/2/2024 9:17 AM | |
Joined: 3/27/2008 Last visit: 11/3/2024 Posts: 1144 Rating: (142) |
Do you have a wire link terminals 3 to 4? This provides the reference for the 0/10Volt analogue. Tractor |
Tractor |
|
3/2/2024 11:22 PM | |
Joined: 3/13/2019 Last visit: 11/6/2024 Posts: 174 Rating: (2) |
Dear sir, Thankx for reply, but i have just linked terminal 2 and 3 as per drawing ..... Regards, Pankaj Tiwari |
Follow us on