5/23/2023 8:02 AM | |
Joined: 2/28/2008 Last visit: 7/11/2024 Posts: 243 Rating:
|
|
5/24/2023 6:22 AM | |
Joined: 8/3/2009 Last visit: 7/11/2024 Posts: 13280 Rating:
|
Hello jthyge1 Yes it works I would use the SCADA Export Tool: LINK Then I created a UDT in the PLC (S71500) and use it in an optimized DB Then do an export of the PLc with SCADA Export. -> In Tag Management-> Select the Connection-> AS Symbols-> Load from file (select the export file) -> then go back to Tag view-> create a new struct (only the name)-> AS Sructures -> then udts/sructs from the PLC are created and you can select your struct for "WinCC Stucture" -> Then you can select the whole struct/udt in the AS Symbols view (not just the single tags) If my explaination was to confusing https://support.industry.siemens.com/cs/de/en/view/101908495 Since V7.5 SP2 you can use udts directly. Bye Murof
|
Last edited by: Murof at: 05/24/2023 06:24:45Last edited by: Murof at: 05/24/2023 06:27:33Last edited by: Murof at: 05/24/2023 06:27:45If this Information really helps, you could use the Rate function |
|