8/31/2005 3:21 PM | |
Joined: 8/10/2005 Last visit: 4/9/2024 Posts: 1486 Rating: (32)
|
Dear Mr. Sadrud if you choose quick parameterization you are asked to set parameter P368 to a certain setpoint source. If you choosed e.g. "1", you operate the drive via analog input and terminal strip. If you set P368 = 6, you operate the drive via PROFIBUS DP. I don't know your setting, so lets take P368 = 1: In this case the OFF2 signal comes from terminal X101:8. If X101:8 is 0V, the display shows °008 (power inhibit). As soon as you jumper X101:8 to X101:1 (+24V), "H", the display will show °009 (ready to power-up). Please refer to the operating instructions, pages 9-11, 9-14, and 9-21 |