2/13/2016 4:00 PM | |
Joined: 9/27/2006 Last visit: 8/30/2024 Posts: 12280 Rating:
|
Hello Kreso; If you are looking for a Siemens solution, on your ET 200M station you could setup a CP 341 (there are different models, RS-232 or RS-485) with a Modbus RTU master to communicate with the Modbus slave on the burner. See the driver information: SIMATIC S7-300/S7-400 Loadable Driver for Point-to-Point CPs: MODBUS protocol, RTU format, S7 is master https://support.industry.siemens.com/cs/ww/en/view/1220184 This can be an expensive solurion, because the driver requires a license (and a physical dongle in the CP 341) to function. You could also add a ET 200S station (much less expensive) with a 1SI serial module to your Profibus-DP network; this module supports Modbus master directly without a required license. SIMATIC ET 200S Serial interface modules https://support.industry.siemens.com/cs/ww/en/view/9260793 If you prefer a gateway solution between Profinet and Modbus RTU, there are a variety of these available from different manufacturers: https://www.google.ca/?gws_rd=ssl#q=profinet+modbus+gateway Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 2/13/2016 10:53:54 PM |
|
This contribution was helpful to
1 thankful Users |
2/16/2016 5:25 PM | |
Joined: 6/26/2009 Last visit: 8/6/2024 Posts: 122 Rating:
|
Hi Kreso , some things to deal with : maximum 20 registers can be read per sequence. In the manual the registers starts at 0 , in fact that is holding register 40001 for your PLC. We did it also with a S7-1200 and a modbus RS232 to modbus TCP converter , delivered from weishaupt you will find the modbus manual here , and the tcp gateway link |
This contribution was helpful to
1 thankful Users |
8/26/2017 7:46 AM | |
Posts: 21 Rating:
|
hi kreso i need AZL Module modbus register detail can you please give some document . the link you previously post did not work best regard |
8/26/2017 11:49 PM | |
Joined: 9/27/2006 Last visit: 8/30/2024 Posts: 12280 Rating:
|
Hello Bukhari; This manual located on the web might provide what you need: AZL... Modbus User Documentation - Siemens Hope this helps, Daniel Chartier |
10/13/2017 12:23 PM | |
Joined: 1/23/2013 Last visit: 8/10/2022 Posts: 226 Rating:
|
Hi CC1J7556en manuals Modbus S7-1200 AttachmentDownload.aspx.pdf (650 Downloads) |
This contribution was helpful to
1 thankful Users |
Follow us on