Hello Mr. Geo, Welcome to forum. Alarm no 608 - is speed controller at its limit for longer time set in p1605. Since you mentioned, this problem triggers daily when you restart the machine & all other possible causes have been tried out, I suggest you below points. 1. Check that axis if any external brake or overloading is causing at start. 2. Check the DC bus value, if it is getting develop late. Check & tight the connections of DC bus links, motor cable, motor terminal etc. etc. 3. Check motor IR value & cable for any short circuit, specially motor cable insulation damage. 4. Try by swapping drive LT module of same capacity with another LT module & check if problem shifts. Hope this helps. |