Joined: 11/26/2013 Last visit: 6/5/2024 Posts: 6 Rating: (1) |
SOLVED!!! My situation TIA 16 getting this error / WIN7 64 Solution STEP 1: installing all panel images form the WinCC DVDs, like this guy suggested. STEP 2: install the last version of updates for TIA 16 https://support.industry.siemens.com/cs/document/109746530/image-downloads-for-hmi-operator-panels?dti=0&lc=en-DZ in my case: Unified_Comfort_Panel_Images_V16_Upd6.exe (1,3 GB) plus 109746530_SIMATIC_WinCC_Panel_Images_V16_Upd4.exe (1,9 GB) Another important point for TIA 15.1: Check to have installed the right image like 15.0.0.0 not 15.0.0.5 ( other issue in the past have fun |
This contribution was helpful to4 thankful Users |
3/10/2022 5:29 PM | |
Joined: 1/31/2022 Last visit: 1/16/2024 Posts: 1 Rating: (0) |
Solved I did what "AutoGen_444304" wrote! thank you |
4/12/2022 10:30 AM | |
Joined: 3/23/2022 Last visit: 5/21/2024 Posts: 9 Rating: (0) |
Hello I slove this issue with this way. 1. update HMI panel from 15 to 16. 2. download again Done |