6/22/2010 9:49 AM | |
Posts: 2 Rating: (0) |
Hi grudziu, I'm manager of the GAMMA training center @ Siemens. I guess you probably misunderstood how to link the pushbuttons to the actuator function of ther UP 560, because normally it is easy to establish the local operation. On this device you have 3 functions: 2x sensor (the two rockers of the button) and the actuator (the relay). So when linking both internally you must slide both switches up for the programming mode. Did you try this already ? Did youread the technical manual of the device? The clue is, that the sequence matters: First K3, then K1. If you do it vice versa, it won't work. See https://www.automation.siemens.com/et-static/html_76/search/ftp/bma/5wg35602ab01_bma_d-gb-f-nl-e.pdf It also doesn't make a difference what kind of push button you use - with or without LED is for the UP560 always the same! If yes, and it still doesn't workI'd say, you rather contact the hotline than the forum, because there you'l find the real experts for that system! Either call +49 911 895 7222 or open the web email support request site under www.siemens.com/automation/support-request Best regards Axel Grossmann eibdoktor |
6/23/2010 12:20 PM | |
Posts: 2 Rating: (0) |
Hi, grudziu, the LEDs aren't controlled in the RF system. They simply don't work, so it makes no sense to buy such buttons. Best regards eibdoktor |