5/13/2024 3:01 PM | |
Joined: 8/24/2021 Last visit: 8/21/2024 Posts: 3 Rating: (0) |
Hello, I have the same problem with a KTP1200 Basic 6AV2123-2MB03-0AX0. When switching OFF/ON or End run time and starting again with the USB it keeps rebooting, but when I unplug the USB stick the HMI starts normally. I use the USB for backup purposes but now I can not use it, otherwise the HMI keeps rebooting. Did you find any solution? ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 05/14/2024 05:42:35New subject after splitting |
|
5/14/2024 2:06 PM | |
Joined: 5/6/2022 Last visit: 11/7/2024 Posts: 487 Rating: (97) |
Hi Bri43, What USB device are you using? I'll tell you if it's an official Siemens one or not. Do you have the reference that comes in the Basic manual?: "SIMATIC HMI Operator Panels Basic Panels 2nd Generation: Accessories" Have you tried resetting the panel to factory settings and installing the latest available image version? Best regards! |
If this Information really helps, you could use the Rate function |
|
5/14/2024 2:06 PM | |
Joined: 2/17/2020 Last visit: 11/7/2024 Posts: 1111 Rating: (203) |
Hi, Does the USB device meet the requirements detailed in the manual? Basic Panels manual - Connecting a USB device The KTP1200 Basic technical sheet also indicates that the USB must have a maximum capacity of up to 16 GB, so please make sure that you are not connecting a USB with a larger capacity. |
A rating will be well appreciated. |
|
Follow us on