Hi, Depending on the environment in which the OP7 is programmed, whether protool or wincc flexible, you will have to make several jumps to migrate to TIA portal with a KP400: SIMATIC HMI HMI devices Comfort Panels Migration Guide At the CPU level, you would not have to change anything, since you can continue to communicate the KP with the S7-300.
|
If this information really helps, you could use the Rate function. |
|
This contribution was helpful to1 thankful Users |
7/11/2024 12:25 PM | |
Joined: 8/3/2009 Last visit: 11/7/2024 Posts: 14112 Rating: (1767)
|
Hello Yes you have to migrate your Protool project with WInCC flexible 2008 SP2 or older: https://support.industry.siemens.com/cs/ww/en/view/18796902 then change the device to one that exists in TIA V14 -> then to TIA (Already suggested) and then you can change to a device or Version that is supported also in the newer TIA Versions Bye Murof |