Hi. It depends if you are using same hw interface to communicate to modbus partners the "InterfaceID" should be the same, if you are using for example for 1 partner the cpu network port and for other a CP module, the "InterfaceID" should be different. For connection ID it is an unique number to identify the connection. see attached manual on pag. 25 Regards. Attachmentnet_modbus_tcp_s7-1500_s7-1200_en.pdf (562 Downloads) |