On principle it is possible to navigate in trend view in runtime. Please select check box "Online operation" to display the buttons for operating the trend view. This means that you can navigate in the trend view at run time. For more informations about archiving in ProTool please take a look to following link: http://support.automation.siemens.com/WW/view/en/5155752 Please note system-limitations for windows-based panels: (Table in FAQ) Note on CE devices (TP 270, OP 270, MP 270B, MP 370): These panels are not primarily designed for periodical archiving of data, but rather for archiving non-periodically occuring errors (e. g. fault and operation messages). These panels are not designed for comprehensive archiving tasks with quantitites of a higher orders, or with higher requirements to performance. Please note the stated maximum value "Entries per Archive" holds per archive including all Follow-up Archives. Your Technical Support for Automation & Drives SIEMENS AG |
Last edited by: Sabine_Moderator at: 10/4/2005 4:25 PM |
|