Joined: 10/3/2023 Last visit: 11/2/2024 Posts: 43 Rating: (0) |
Hi experts, I have MP377 HMI version (01.00.36.00). It's not booting and it's stuck in the same screen asking image update.I have prosave v16 and wincc flexible 2008 SP5 I tried reset to factory settings. but i don't know the IP address of HMI. Also, if i enter the MAC address in the OS update. It showing error on interface parameter assignment. How can i update my image without knowing the IP address. attached image for your reference. AttachmentNew folder.zip (281 Downloads) |
6/20/2024 11:42 AM | |
Joined: 8/3/2009 Last visit: 11/7/2024 Posts: 14112 Rating: (1767)
|
Hello Riyasa I the very most cases you can do a OS Update with reset to factory settings using the MAC address if you do nlot know IP or if the panel is not booting in case of a MP377: https://support.industry.siemens.com/cs/ww/en/view/19701610 Bye Murof |