Hi I have a problem with accessing a Micromaster 440, part # 6SE6440-2UE17-5CA1, trying to access it via RS485- USB interface via Siemens STARTER V5.4.2.1. I cannot access the VFD as a slave/node (see error attached) , just does not pick it up, any help/ guide can be of use. Regards M.Zulu ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 03/02/2023 08:23:13New subject after splitting |
|
3/3/2023 3:51 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (878) |
Hello, In RS-485 communication power supply must be available using pull up/pull down resistors. Please check if these resistors are connected so that RS485 communication can be active. Please refer 6SE6400-5AW00-0BP0 for more details. |