Hi trabde, In other cases, I have been able to see this behavior because of the process image that encompasses these computers. In this case, the IM151-8 PN/DP CPU comes with a default I/O process image size of 128 bytes and the address you are trying to access is 272...275 so the process image cannot read it. Therefore, you need to increase it to reach that number from the CPU properties > Cycle. The limit, if I remember correctly is 2048, but I recommend that you increase it by the addresses you want to read so as not to affect the duty cycle. Best regards! |