Dear Experts As I mention before I have a problem with replacing CP50M0 with CP50M1 and I a bit desperate :) Let me explain my case: I have TDC rack with several CP50M0 which I need to replace to CP50M1 from obvious reason Basically profibus lines are:
Let’s concentrate on the last one case. I replace CP50M0 with CP50M1 and did necessary HW modification on TDC side. S7 side I leaved untouched. My configuration of TDC is shown in files:
TDC Software configuration shown in files:
S7 configuration is shown in files:
Profibus line is scanned and looks ok:
On TDC side in card D2000C X1 and X2 interfaces are configured as a 2 different slaves on the same profibus network. For test purpose I connect or X1 or X2 interface to S7. What is interested it das not matter which interface is connected to S7 on both of them I have the same fault on CRV block - #6012 Any Idea what I’m doing wrong? Thank you for your help. Oh is possible to add only 1 file - please find all of pictures in atched pdf. Regards Marcin AttachmentTDC_problem_comm_s7.pdf (937 Downloads) |
1/18/2022 10:43 AM | |
Joined: 8/25/2006 Last visit: 11/6/2024 Posts: 2211 Rating: (280)
|
Hello. Look at application example how to configure CP50M1 as slave. You need to combine S7-project and TDC-project into one project. At CRV/CTV FB's you need to correct AR/AT connectors like this: MGU2MD.0.1 and U2MGMD.0.1. "0" means that this channel is slave. |