I have a similar issue with 1517F. Wneh I switch off the power supply and switch on again the PLC dosen't switch in run mode automatically it's necessary move the PLC switch in stop and put it in run again. Into Buffer diagnostic i see event 16# 02: 4468 Could be necessary replace the device? Thank you Regards. ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 12/28/2022 13:20:36New subject after splitting |
|
12/28/2022 2:44 PM | |
Joined: 7/7/2010 Last visit: 5/17/2024 Posts: 14751 Rating: (2377) |
To me, the more disturbing event and the root cause of the issue is that the PLC's power supply was overloaded and forced the PLC into "power off" mode even while input voltage was still applied. You may want to add an additional or larger PS/PM to the system. Consult the PLC hardware configuration to see how close the system is to using all available power during peak power consumption.
|