Hello Furkanayeng redarding Device Updates od HMIs there is not always a new Device Version in TIA Portal settings for every Image Version for the Panels. Only if there are implemented new features that have an influence also the engineering sytem there is a new Device Version to select in TIA. On the Panel there has to be at least the in TIA Selected Version but you can also use a newer Update version. For example if an Update do only have bugfixes there is no new Device Image Version in TIA. So in your case you cannot change to a newer V19 Device Version as V19.0.0.2 -> ALSO if there is a newer V19.0.0.3 Image for the Panels available -> so this is a normal behaviour Check the Table in Chapter 2: https://support.industry.siemens.com/cs/de/en/view/109746530 Bye Murof |