Hello ixo65, I have a threshold trigger that is not activating. The mathematic instruction block is enabled. I also noticed that the Aq value at the mathematic instruction block is showing 0. But when online and I click the goggles the value is there.
It is set to trigger at 36 meters for my application, but it isn't working. I've tried different values changing blocks but I'm obviously missing something simple. I have used this process a lot and I have never struck this problem. Same software, V8.4.0. Logo modules both the same 6ED1052-1HB08-0BA2. Any help appreciated. Thanks, ------------------------------------------------------------------------------------------ AttachmentVacuum Interlock Project 2024_scrap function (2).zip (201 Downloads) |
Last edited by: Moderator_Lan at: 06/06/2025 06:34:29New subject after splitting |
|
6/6/2025 2:27 AM | |
Joined: 12/18/2014 Last visit: 9/15/2025 Posts: 35964 Rating:
|
Your problem is that the input value to the analog threshold trigger B011 changes in steps of 14. If the counter value of B010 is then incremented by 1, the analog threshold trigger B011 receives the value 3612 (258 x 14 = 3612). This value is higher than the OFF parameter. Result: The analog threshold trigger B011 can therefore never switch on.
|
Last edited by: ixo65 at: 06/06/2025 02:28:40 |
|