Dear experts . Is it possible to download HW without putting my PLC in stop mode???
|
4/25/2012 7:57 AM | |
Posts: 153 Rating:
|
thanks a lot, well I am using 412-2dp with software redundancy, In this I can download my HW in cpu one by one ???or not |
4/25/2012 8:30 AM | |
Joined: 8/27/2006 Last visit: 5/14/2024 Posts: 719 Rating:
|
I think changing the HW configuration to the CPU rack is not possible in Run mode, however, the CIR (Configuration In Run) capability for some slaves enable you to change the HW configuration of slaves during run. You may want to check this http://support.automation.siemens.com/BR/view/en/14044916 Mentioning that you have a redundant CPU, then you can stop one, download the new configuration and make it the master, then stop the other and download the new configuration
|