3/15/2016 11:27 AM | |
Joined: 8/25/2006 Last visit: 9/4/2024 Posts: 2208 Rating:
|
Hello. Rated armature voltage of motor is set via P101, also check all start-up procedure (including optimization runs) in the manual, chapter 7.5. |
3/25/2016 7:24 AM | |
Joined: 8/25/2006 Last visit: 9/4/2024 Posts: 2208 Rating:
|
Hello. What are the rated motor data? |
3/25/2016 8:15 AM | |
Posts: 57 Rating:
|
KW: 7.5 Arm Volt: 400V Arm Current: 21A Field Voltage: 220V Field Current: 1.56A RPM: 1500 |
3/25/2016 8:30 AM | |
Joined: 8/25/2006 Last visit: 9/4/2024 Posts: 2208 Rating:
|
Did you make speed controller optimization (P051=26) after P051=25? |
3/25/2016 8:54 AM | |
Posts: 57 Rating:
|
yes |
3/25/2016 9:52 AM | |
Joined: 8/25/2006 Last visit: 9/4/2024 Posts: 2208 Rating:
|
May be you need to make manual optimization of speed controller to remove fluctuations. 3. Did you check P115? 4. By default in 6RA70 P082=2 (standstill field after line contactor drop). Check the value of P257 or use P082=1 or 3. |
3/25/2016 12:25 PM | |
Joined: 2/9/2013 Last visit: 1/6/2024 Posts: 11 Rating:
|
check the actual Field Resistance after removing motor terminals using meter. |
Follow us on