10/28/2016 10:42 PM | |
Joined: 7/30/2012 Last visit: 5/7/2024 Posts: 127 Rating: (0) |
OK i am not sure the issue is because of this OB or not ill explain the whole scenario in breif an FB is being called in and FC which is then being called in OB35. what if i delete this OB 35 online and call the FC that is being called in OB35 in OB1 what will be the impact why the programmer's use OB35 is it to safe processor from continuous processing and being busy.. i did this actually i deleted this OB35 along with the FC's in it and called those FC's in OB1 but the outcome was same as it was before when those FC's were in OB35 means not working properly code attached for reference... please guide what should be done should i download the whole logic in some sequence or look for something else. by sequence i mean download DB's firsr then FB then FC and then OB... Attachmentpower_ho.zip (113 Downloads) |
10/29/2016 10:57 PM | |
Joined: 1/21/2013 Last visit: 6/6/2024 Posts: 4620 Rating: (705) |
Dear List, I have several CPUs 315-2AF03 and 315-2AG10 that have as OB35 --> 5 ms and OB1 which runs on 12-14 ms and I have no problem, the only problem is that you can not go online in OB 35 because go to STOP as cycle time exceeded or you want to know what happens if you exceed this time? look below: http://www.infoplc.net/files/descargas/siemens/infoplc_net_sitrain_12_obs.pdf
|
Last edited by: Ste39 at: 10/29/2016 11:00:20 PMLast edited by: Ste39 at: 10/29/2016 11:05:06 PM |
|
This contribution was helpful to2 thankful Users |
Follow us on