6/4/2011 2:16 AM | |
Joined: 7/2/2008 Last visit: 4/5/2024 Posts: 928 Rating: (305)
|
Hello engrosa, It will be better if youupload your diagnostic buffer, PLC software and OP software. At least the diagnostic buffer may help to make sure you have nothing wrong with hardware. Best regards. H-H |
6/4/2011 9:11 PM | |
Posts: 947 Rating: (45) |
I agree H-H. Very difficult to correctly answer without diagnostic buffer. |
6/6/2011 1:13 AM | |
Posts: 7 Rating: (0) |
dear friend thank you for help problem solved by 1-if you see drive block you will see spare bit 31 i followed these line until found block to run machine and these block input from module 322-1HF10-0AB0 and these input conenected to one switch wok by key after chang key and on then problem solved same emergency swith i check all control word all db all hex value in wincc and final problem solved by one switch thank you for understanding and cooperation engrosa Attachment1.zip (35 Downloads) |
This contribution was helpful to2 thankful Users |