Dear Adi COM15 communicated on Profibus network.Baud ratedepends on the length of the profibus cable length. You can find all details of profibus in the Manual at the link below : http://support.automation.siemens.com/WW/view/en/35222591 As a thumb rule, if your network length is < 100meters and for upto 31 breakers, 1.5MBPS should be OK. However it is better to check the exact data before deciding the Baud rate Hope this helps Regards Navnag |