8/4/2010 8:22 AM | |
Joined: 10/7/2005 Last visit: 5/20/2024 Posts: 3005 Rating: (1048) |
Hello Gerwenr it means that you also need to set the "Acquisition mode" for the tags to cyclic continuous or on demand. Note that "Acquisition mode" is different to "Logging Acquisition mode". Have a look at "general' section of the Tag properties window in the bottom half of yourscreendump, you'll see that the "Acquisition mode" for the selected tag is set to "Cyclic on use" rather than cyclic continuous or on demand. I hope this helps |
Cheers |
|
8/4/2010 11:40 AM | |
Posts: 18 Rating: (4) |
It worked. Thanks a lot. |