Hello, am also converting one HMI OP177B which is communicating to D445 To KP700 Comfort. project is integrated project with step7, scout v4.2, wincc flex 2008 sp2. Now need to migrate only HMI to new. LAPTOP1-> STEP7,WINCC FLEXIBLEm2008 sp3, WINCC COMFORT v13 sp1, SIMOTION SCOUT V4.4 LAPTOP2-> STEP7, WINCC FLEXIBLE 208 sp3, WINCC ADVANCE V13 SP1, SIMOTION SCOUT TIA V 4.4.0.5
Do i need to install both stand alone and TIA scout in same laptop or am missing something else ? also any additional plug in software for scout migration required ? kindly suggest ------------------------------------------------------------------------------------------ |
Last edited by: Min_Moderator at: 5/30/2016 11:35:27 AMNew subject after splitting
|
|
5/27/2016 3:25 PM | |
Joined: 5/12/2006 Last visit: 10/22/2024 Posts: 22431 Rating: (3029)
|
Herllo, yes for the proxy you need both versions installed on the same computer.
Christoph |
5/28/2016 11:33 AM | |
Joined: 9/2/2012 Last visit: 8/15/2024 Posts: 711 Rating: (30) |
or is there any alternate option to solve the issue ? |
|
|
5/28/2016 12:19 PM | |
Joined: 5/12/2006 Last visit: 10/22/2024 Posts: 22431 Rating: (3029)
|
Hello, if you use both in the same version then there is no compatibility problem. the latest versions you can download here: https://support.industry.siemens.com/cs/ww/en/view/109480713 If you must use the device Proxy there is no other solution. A migration of he whole project is only possible if you use a SIMOTION D which is supported in the Scout TIA (D4x5-2)
Christoph |