I did as you wrote, everything works fine. Thanks a lot.
------------------------------------------------------------------------------------------ Attachmentzdjecia tia.zip (326 Downloads) |
Last edited by: Jen_Moderator at: 02/05/2024 07:43:24Text formatting optimized. Last edited by: Jen_Moderator at: 02/05/2024 07:45:44New subject after splitting |
|
2/2/2024 9:39 AM | |
Joined: 12/18/2014 Last visit: 10/19/2024 Posts: 33993 Rating: (4226)
|
If you want a display with a decimal point, then must you the measuring range with 10. Is your measuring range -40 to 85 °C, then must you set the minimum to -400 and the maximum to 850. Then is the the measuring -40,0 to 85.0. The problem is that the LOGO! only knows integer values. And want you see negative values on the HMI, then must set in the HMI tag table of TIA the data type to Int, not word. AttachmentWarsztat_System_chlodzenia.02.02.2024_ver2.zip (381 Downloads) |
This contribution was helpful to1 thankful Users |
2/5/2024 9:50 AM | |
Joined: 12/27/2018 Last visit: 2/5/2024 Posts: 14 Rating: (0) |
In B042 my measuring range -40 to 85 °C, so I set the minimum to -400 and the maximum to 880 becouse I want to displey it on a panel in decimal . It works ok. I don't know how to select the correct parameters in b043. for example I would like to enter on a panel a value in minusue: -10 to +30 with an accuracy of 0.1 AttachmentWarsztat_System_chlodzenia.05.02.2024_ver1.zip (336 Downloads) |
2/5/2024 11:47 AM | |
Joined: 12/27/2018 Last visit: 2/5/2024 Posts: 14 Rating: (0) |
ok it;s works :) |