4/8/2023 9:14 AM | |
Joined: 3/30/2020 Last visit: 8/14/2024 Posts: 4695 Rating: (975) |
The way that you trigger the 'zero' is of importance here. Sharing your code by a screen capture would be helpful. My guess is that you are attempting to read the Z-phase input through a normal program. The input is triggered for a very short time. The PLC cycle exceeds this short time. Plus the filter time for the input is not set correctly in the hardware configuration. Assuming you have a current generation S7-1200 coded with a current generation Step7 -- Link the Z-phase input to the 'sync input' in the hardware configuration of the HSC you are using. Helpful? Late note: Attachmentextract_sync-input.pdf (346 Downloads) |
Last edited by: qwazee at: 04/08/2023 09:16:57add a PDF page extracted from the essential system manual Last edited by: qwazee at: 04/08/2023 09:21:24add a late note Activities of this user is voluntary. There is no obligation or liability placed on this user. Though optional, your 'please' and 'thank you' is highly valued. |
|