6/3/2022 1:12 AM | |
Joined: 10/21/2005 Last visit: 10/30/2024 Posts: 5 Rating: (0) |
Dear Team, Thank you for your prompt response, I have verified in STARTER that both online and offline P3925[0].0 is active at 1 (P340=1 or P3900>1). After completing the offline Wizard of the motor when you transfer the parameters to the drive, you notice that you must manually execute P340=1 since there are certain motor data that were not modified with the download, for example P341 and P344, etc. Attached is the list of parameters that differ online-offline with manual online activation of P340=1. Could it be that when the Starter transfers the parameters to the drive with P340=1 activated, the drive calculates the mathematical model only with the values up to P340 and the values located above this number, for example P341, P344, etc. are ignored? Do I have to run online manually P340=1 or P10=1->p3900=3 to be sure of loading the model? The motor is a 1NA1458-6AC00-0AA0 (1MW-690Vac) and the drive is a G150. I have not checked if this happens with another series of motors . B.R. Pablo AttachmentP003A.pdf (567 Downloads) |