8/9/2012 6:14 PM | |
Joined: 9/27/2006 Last visit: 7/7/2024 Posts: 12268 Rating:
|
Hello krneki10; What value do you send to the Analog Output address? The nominal range is 0-27648 (unipolar)or +/- 27648 (bipolar) for all Siemens analog input and output modules. If you are using a unipolar range of 0-10V, a numerical value of 0 will output 0 V, a numerical value of 27648 will output 10V; however in overflow (a value of more than 32000) will output almost 12 V. See the attached screencapture, from the S7-400 module data manual: SIMATIC S7-400 S7-400 Automation System Module Data There are instructions in Step 7 to manipulate analog data; they are located in the TI-S7 converting blocks library. They are: |
8/9/2012 7:39 PM | |
Joined: 4/22/2010 Last visit: 5/3/2024 Posts: 5697 Rating:
|
Hello, Can you show us the program you created, by printscreen or pdf printout? there are many threads about Fc105(6) one is here. with some examples. Regards, Marcjan |
Problem solved? |
|
8/9/2012 10:43 PM | |
Posts: 45 Rating:
|
Well, there is not really much to show. For a start I'd like to create simple ladder program where I will be able to set voltage from 0 to 10 V manually. As I already said, I tried to do that with MOVE ladder element, but without success. Afterwards, I will connect S7 to AEG module, please see attached file. Original (pdf) is in German, .doc is translated with google. As you can see, I will control input voltage with potentiometer, but it must be in range 0 to +10 V. Here are product numbers:
Attachmentaeg_module.zip (191 Downloads) |
Last edited by: krneki10 at: 8/9/2012 10:44 PM |
|
8/10/2012 8:01 AM | |
Joined: 4/22/2010 Last visit: 5/3/2024 Posts: 5697 Rating:
|
Hello, See attached pdf. Solution by using scale and unscale function. Regards, Marcjan AttachmentFC1-scale-unscale.pdf (255 Downloads) |
Problem solved? |
|
8/10/2012 12:26 PM | |
Posts: 45 Rating:
|
Hello, I've tried your program. I created FC1 block and inserted FC105 and FC106. Please see file attached. Then I put FC1 into OB1, but obviously I have no idea how to call FC1. If I don't put anything on input (EN), I will get error. The same goes for output ENO. I've only managed to download program when I used normaly open contact I0.0 for EN and Q0.0 for ENO, but since I0.0 will always be on 0, program won't work. I've also tried merker M0.0 instead of I0.0, but as soon as I modify it to 1, SIMATIC just goes to STOP mode. Oh, and by the way, what is up with this link:https://support.automation.siemens.com/WW/adsearch/resultset.aspx?region=WW&lang=en&netmode=internet&ui=NDAwMDAxNwAA&term=6ES7432-1HF00-0AB0&ID=14340592&ehbid=14340592? Will that force my PLK to use nominal values instead of overflow?
AttachmentFC1.pdf (209 Downloads) |
Last edited by: krneki10 at: 8/10/2012 12:36 PMLast edited by: krneki10 at: 8/10/2012 12:27 PM |
|
Follow us on