Hello, do you parameterize the DI of the module? (set function of DI) Please check this. Here is also a manual for counting with TM SIMATIC S7-1500, ET 200MP, ET 200SP, ET 200AL Counting, measurement and position detection Hope this is helpful for you. regards |
3/21/2023 8:03 AM | |
Joined: 4/28/2015 Last visit: 8/7/2025 Posts: 399 Rating:
|
Hello, please have a look to the manual SIMATIC ET 200SP TM Count 1x24V (07/2019) I think, you have to open the hardware gate (DI0 - chapter 3.1 - Digital inputs DI0, DI1 and DI2) and the software gate (SW_GATE - Chapter 4.3.5.1 - Control interface) for counting (see Chapter 2.2.1 - gate control)... |
3/22/2023 12:40 PM | |
Joined: 12/6/2022 Last visit: 12/12/2023 Posts: 4 Rating:
|
Hello, Thanks for your response, I'm using PCS7 9.0 SP2, for Software gate Configuration, is there any Technology block available?. Since there is no wiring connection available for DI Channels in the module. So, I've configured all DI Channels as "Digital Input Without Function". Is Hardware Gate Configuration is mandatory for Calculating the RPM using Pulse A Signal?. Please suggest mandatory wiring option for calculating the RPM using this Module. |
8/2/2023 1:17 PM | |
Joined: 10/30/2022 Last visit: 8/4/2023 Posts: 1 Rating:
|
I have de same problem. Have you got a solution? Please help me |