Hi Strini, I recommend you review the following FAQ, it will help you: With SIMATIC WinCC (TIA Portal) on a panel, how do you access process data in a file via a script? |
If this information really helps, you could use the Rate function. |
|
8/25/2023 11:33 AM | |
Joined: 9/10/2012 Last visit: 6/28/2024 Posts: 68 Rating:
|
Thanks, but it's not what I looking for. |
8/29/2023 11:49 AM | |
Joined: 8/3/2009 Last visit: 7/17/2024 Posts: 13308 Rating:
|
Hello Strini No this is not possible. you cannot get access to the Panel Filesystem from "outside" (only with miniweb as described in you first post) Only workaround would be to copy the file cyclic to a network share (by the HMI Rutnime on the Panel) the PC has also access to. you can integrate the Panel to network and also share data like this: https://support.industry.siemens.com/cs/ww/en/view/92346478 Bye Murof |