2/13/2013 7:35 AM | |
Posts: 13 Rating: (0) |
Dear experts, i am using HART AI module 331-7TF01-0AB0. I need to receive hart data from 4 promag 50 flow meters from E&H. I have configured the hard device with PDM and there is no fault LED for channel 0 to 3. I have added SFC 58 & 59 but i cannot receive data and it gives error code in RET_VAL which i have mentioned below. I have attached the screen shot also. My AI module starting address is 972 so in LADDR i have given W#16#3CC. I am receiving some fixed values in the DB81 for SFC 59. Error codes in SFC 58: 7001, 7002, 80b0 Error codes in SFC 59: 7001, 7002, 80c3 & 8. in both SFC's BUSY is always toggling from 0 to 1 and vice versa.
AttachmentHart-test.zip (90 Downloads) |