I am getting issue in my TP177A siemens hmi. I had once upgraded the OS version, and after the up gradation My HMI Screen goes in blue color. What should I do know. I had Tried all the possible way to resolve this issue. ------------------------------------------------------------------------------------------ |
Last edited by: Prasad B at: 01/11/2024 12:39:09Last edited by: Jen_Moderator at: 01/12/2024 08:53:51New subject after splitting |
|
1/23/2024 10:18 AM | |
Joined: 8/3/2009 Last visit: 6/19/2024 Posts: 13078 Rating: (1660)
|
Hello Prasad B If the Panel does not load to operating system you only could try to do a Reset to factory settings with prosave: https://support.industry.siemens.com/cs/ww/en/view/19701610 If this does not work, I guess you have to send it to repair center Bye Murof |