6/25/2015 5:08 PM | |
Joined: 9/27/2006 Last visit: 9/2/2025 Posts: 12397 Rating:
|
Hello drmandge; The PM571 supports Modbus/TCP communications, so the easiest way would be to setp the S7-300 CPU as a Modbus/TCP client using its integrated PN port. Datasheet Of PM571: http://www.abb.com/SmartLinks/Default.aspx?gid=ABB1SAP130100R0170
Presentation of Open ModbusTCP librairies for Siemens S7 PLCs: You will nee the license for PN CPUs, 2XV9450-1MB02 Manual for Open ModbusTCP: PN Library download (Demo mode): Block library for Modbus/TCP communication over the integrated PN interface of a SIMATIC CPU
Example programs for Open ModbusTCP:
Hope this helps, Daniel Chartier |
10/5/2017 9:31 AM | |
Joined: 6/19/2017 Last visit: 9/6/2024 Posts: 8171 Rating:
|
New question published by qwer_F is split to a separate thread with the subject S7-300 communication with ABB - in PLC no FB Modbus/tcp/slave. Best regards |