5/13/2014 12:01 PM | |
Joined: 11/26/2011 Last visit: 6/29/2023 Posts: 508 Rating: (22) |
In Simple words, 10 % increase in voltage gives you 50 % increase in excitation current iscalled knee point voltage. ForCalculationlink 2you can find more links on internet. |
This contribution was helpful to1 thankful Users |
5/13/2014 1:25 PM | |
Joined: 11/26/2011 Last visit: 6/29/2023 Posts: 508 Rating: (22) |
You are correct. It s the saturation point of CT. |
5/13/2014 2:14 PM |
|
Posts: 235 Rating: (52) |
Dear Madhava, Thanx for your reply but i cant found any calculation on your mentioned link pls help for calculation its very argent for me. |
5/14/2014 10:36 AM |
|
Posts: 235 Rating: (52) |
Dear all, Thanking you for your valuable feedback. Finaly i got how to calculate Ct knee point voltage here is the attched file for calculation AttachmentCT Knee point voltage calculation.pdf (1839 Downloads) |
Follow us on