5/18/2015 4:01 PM | |
Posts: 15 Rating: (0) |
With these features now available with FW V4.1, is it possible to use the PLC open function simply for start/stop and speed control of the G120? Is there a way to use them without encoder feedback?
---------------------------------------------------------------------------------------------------- |
Last edited by: Min_Moderator at: 5/19/2015 11:55:16 AMNew subject after splitting |
|
5/20/2015 6:06 PM | |
Joined: 8/31/2005 Last visit: 11/13/2024 Posts: 2198 Rating: (328) |
You can use the technological functions, but you need a encoder feedback. You should use the SINA_SPEED FB (https://support.industry.siemens.com/cs/ww/en/view/109475044) |
|
|
Follow us on