Here are a example for a 1000mbar blower P0003 = 3 (Expert mod3) set point e.g. P1080[0] = 18 (min.frequenz 18Hz) P1082[0] = 55 (max.frequenz 55Hz) 3. value Analoginput 1= terminal 3/4 pressure value e.g.0 ... 1000mbar, 4 ... 20mA Analoginput 1= 0 - 20mA per DIP Switch 1 ON P0756[0] =2 (current input1) P0757[0] = 4 P0758[0] = 0 P0759[0] = 20 P0760[0] = 100 P0761[0] = 4 4. set point the e.g. 1000mbar= 100% P2201[0] = % (100mbarequals 10%, 500mbar 50% .....) P2216 = 1 P2253[0] = 2224 5. PID-Controler P2200[0] = 1 P2251 = 0 (PID-main set point) P2253[0] = 2224 (connection of PID-setpoint) P2264[0] = 755.0 (connection ofPID-value) P2280 ~ 3 (kP) P2285 ~ 10 (TN)