6/24/2012 1:49 PM | |
Joined: 12/22/2006 Last visit: 1/25/2022 Posts: 1742 Rating:
|
Hello, The S7-1200 supports iso-on-tcp using the blocks TSEND_C, TRCV_C. See the easy book: http://support.automation.siemens.com/WW/view/en/39710145 Chapter 7.5 Or the system mamual: http://support.automation.siemens.com/WW/view/en/49915587 chapter 10.2.2.4 Some example: http://support.automation.siemens.com/WW/view/en/39040038 |
Last edited by: jklm at: 6/24/2012 1:53 PMBest regards |
|
This contribution was helpful to
1 thankful Users |
6/30/2015 6:05 PM | |
Joined: 11/12/2014 Last visit: 10/31/2023 Posts: 11 Rating:
|
Experts, problem solved! TIA Portal V13Sp1, requires TCON block. then the procedure: *Side HMI: Controller: S7-1200(ISO TCP) HMI STATIO:1 PLC STATION:2 CONTROLLER IP:192.168.0.1 PORT:102 *SIDE PLC: Check Box Permit Access With PUT/GET FULL ACCESS(No Protection) Use the TCON(Instructions -> Communication -> Others -> TCON).
AttachmentImages.rar (1675 Downloads) |
Last edited by: DougPin at: 6/30/2015 7:04:16 PMDouglas Silva |
|
This contribution was helpful to
5 thankful Users |
11/30/2016 2:15 PM | |
Posts: 2 Rating:
|
Hi i do all the steps that you explain , but I have a error, can you helpme???
Attachmentfotos1.zip (640 Downloads) |
5/22/2017 2:34 PM | |
Joined: 8/13/2016 Last visit: 6/11/2022 Posts: 3 Rating:
|
|
Last edited by: mustafa1170 at: 5/22/2017 2:35:36 PM |
|
Follow us on