10/27/2014 10:29 PM | |
Joined: 12/27/2006 Last visit: 8/18/2024 Posts: 1197 Rating: (113) |
Its better to use a LOGO whit relaiskontacts. Then you can use everykind of solenoids. You must have a powerunit for your sonenoids, and a powerunit for your LOGO! P.E. use the LOGO 24 RC u can use it on 24 VAC or 24 VDC or use the LOGO 12/24 Rc, thats works on 12 or 24 VDC (not AC) The programm you wishes is an "little egg" for the LOGO. You can easy make it with a LOGO! Its not nessesary to use the newest LOGO OBA8, it works also with an old OBA4
Attachmentballon.zip (160 Downloads) |
Last edited by: Toeternietoe at: 10/27/2014 11:13 PMLook at the attachment for a programm |
|